Skip to main content
Examonaut

Topic 13B · Lesson 2 of 4

Transformer power and current (Higher tier)

Power in a transformerHigher tier

Real transformers are very efficient, close to 100%. For a 100% efficient transformer, power in = power out, and since P=IVP = IV:

Vp×Ip=Vs×IsV_p \times I_p = V_s \times I_s
  • IpI_p is the current in the primary coil, in amps (A);
  • IsI_s is the current in the secondary coil, in amps (A).

This equation is given on the equation sheet. So if a transformer steps the p.d. up by some factor, it steps the current down by the same factor, and vice versa. A transformer cannot give out more power than it takes in.

Worked example

A step-down transformerHigher tier

A transformer has 2300 turns on its primary coil, which is connected to the 230 V mains. The output is 5.0 V. Find the number of turns on the secondary coil.

Show solution
  1. Write the equation: VpVs=NpNs\frac{V_p}{V_s} = \frac{N_p}{N_s}.
  2. Substitute: 2305.0=2300Ns\frac{230}{5.0} = \frac{2300}{N_s}, so 46=2300Ns46 = \frac{2300}{N_s}.
  3. Rearrange: Ns=230046=50N_s = \frac{2300}{46} = 50 turns.

Worked example

Currents in a chargerHigher tier

The same transformer supplies an output current of 1.2 A. Assuming it is 100% efficient, find the current in the primary coil.

Show solution
  1. Power out =Vs×Is=5.0×1.2=6.0= V_s \times I_s = 5.0 \times 1.2 = 6.0 W.
  2. Power in = power out, so Vp×Ip=6.0V_p \times I_p = 6.0.
  3. Ip=6.0230=0.026I_p = \frac{6.0}{230} = 0.026 A (2 s.f.).
  4. The p.d. has been stepped down by a factor of 46, so the current is stepped up by the same factor: 0.026×46≈1.20.026 \times 46 \approx 1.2 A. ✓
primary coil2300 turnsVₚ = 230 VIₚ = 0.026 Asecondary coil50 turnsVₛ = 5.0 VIₛ = 1.2 Airon corepower in = power out: Vₚ × Iₚ = Vₛ × Iₛ = 6.0 Wp.d. stepped down by a factor of 46, so current stepped up by 46

Worked example

A step-up transformerHigher tier

A step-up transformer has 500 turns on its primary and 10 000 turns on its secondary. The primary p.d. is 25 kV and the primary current is 800 A. Find the secondary p.d. and current (100% efficient).

Show solution
  1. Vs=Vp×NsNp=25 000×10 000500=500 000V_s = V_p \times \frac{N_s}{N_p} = 25\,000 \times \frac{10\,000}{500} = 500\,000 V (500 kV).
  2. Is=Vp×IpVs=25 000×800500 000=40I_s = \frac{V_p \times I_p}{V_s} = \frac{25\,000 \times 800}{500\,000} = 40 A.
  3. The p.d. has gone up by a factor of 20, so the current has gone down by a factor of 20.