Topic 10D · Lesson 2 of 4
Fuses, earthing and circuit breakers
Fuses and earthing
A fuse is a thin wire inside a cartridge, connected in the live wire. If the current becomes too large, the fuse wire heats up and melts, breaking the circuit. This stops the cable and appliance overheating and catching fire.
Appliances with metal cases are earthed: the earth wire is connected to the case. If a fault makes the live wire touch the case:
- a large current flows from the live wire, through the case and down the low-resistance earth wire to the ground;
- this large current melts the fuse (or trips a circuit breaker, see below) straight away;
- the appliance is disconnected from the live wire, so the case is no longer at a high potential and is safe to touch.
Without the earth wire, the case would stay at a high potential, and the first person to touch it would become the path to earth.
Appliances with plastic cases that no live part can touch are double insulated. Their case cannot become live, so they need no earth wire and use two-core cable (live and neutral).
Circuit breakers
Most homes now protect each circuit with circuit breakers in the consumer unit (fuse box) instead of fuse wires. A circuit breaker does the same job as a fuse: it is connected in the live wire and switches off automatically when the current is too large. The difference is how it breaks the circuit. Inside is an electromagnet (a coil of wire, see Topic 12) that carries the circuit's current, as the flow chart below shows.
- With a normal current, the electromagnet is too weak to move the iron catch, so the contacts stay closed and the circuit works.
- If the current becomes too large, for example because the live wire touches an earthed case, the magnetic field of the coil becomes much stronger.
- It pulls the iron catch, which releases a spring-loaded switch. The spring pushes the contacts apart, breaking the circuit in the live wire.
- Once the fault has been fixed, the breaker is reset by pushing its switch back; nothing needs replacing.
Compared with fuses, circuit breakers act faster, are easier and safer to reset, and there is no temptation to replace a blown fuse with one of the wrong rating. They are more expensive and more complicated than a fuse. Some breakers (residual current circuit breakers) work slightly differently: they compare the current in the live and neutral wires and switch off very quickly if the two are not equal, because the difference must be leaking to earth, possibly through a person.
Choosing a fuse
The fuse rating must be a little above the normal working current, so it doesn't blow in normal use, but as close to it as possible, so it melts quickly if there is a fault. To choose one:
- find the normal current with ;
- pick the smallest available fuse rating that is bigger than this current (UK plug fuses are usually 3 A, 5 A or 13 A).
Worked example
Choosing fuses
A 2.3 kW kettle and a 450 W television both run on the 230 V mains. Fuses of 3 A, 5 A and 13 A are available. Which fuse should each have?
Show solutionHide solution
- Kettle: A. The smallest fuse above this is 13 A.
- Television: A, about 2.0 A. The smallest fuse above this is 3 A.
- A 13 A fuse in the TV plug would not protect its thinner cable, because the cable could overheat with a fault current below 13 A.
Worked example
A fault in a metal toastertop grade
A 1.15 kW toaster on the 230 V mains has a metal case and the correct fuse (3 A, 5 A or 13 A available). A loose live wire touches the case. The case and earth wire together have a resistance of 0.10 Ω. Explain what happens, with calculations.
Show solutionHide solution
- Normal current: A. The fuse must be rated above this, so it is the 13 A fuse.
- In the fault, the live wire is connected through the case and earth wire to 0 V. Current: A. (In practice the resistance of the house wiring limits it, but it is still huge.)
- This is far above 13 A, so the fuse melts almost instantly, breaking the circuit in the live wire.
- With the fuse melted, the live wire (and so the case) is cut off from the supply, so the case is safe to touch.
- Without the earth wire, there would be no low-resistance path: the fuse would not blow, and the case would stay live until someone touched it.