Skip to main content
Examonaut

Topic 10D · Lesson 1 of 4

Alternating current and the three mains wires

Direct and alternating current

  • Direct current (d.c.): the charge flows in one direction only. Cells and batteries supply d.c.: one terminal is always positive and the other always negative, so the p.d. has a constant direction.
  • Alternating current (a.c.): the charge repeatedly changes direction, flowing one way and then the other. It is driven by an alternating voltage, whose direction keeps reversing.

On an oscilloscope (or a graph of p.d. against time), a d.c. supply gives a flat line on one side of zero, while an a.c. supply gives a wave that goes above zero and then below it.

02040-15015time / msp.d. / Vd.c. (battery)steady 12 V02040-3250325time / msa.c. (UK mains)50 Hz: 1 cycle = 20 ms

The UK mains supply

The UK domestic supply is a.c. at a frequency of 50 Hz and a voltage of about 230 V.

  • 50 Hz means 50 complete cycles every second: the current flows one way, then the other, and back again 50 times a second.
  • The time for one cycle (the period) is 150=0.020\frac{1}{50} = 0.020 s, or 20 ms.
  • The p.d. actually swings between peaks of about +325 V and −325 V. The "230 V" is the steady d.c. p.d. that would give the same heating effect.

Mains electricity is a.c. because it is produced by generators that rotate, and because a.c. can be stepped up and down by transformers, which is essential for the National Grid.

Worked example

Period and frequency

An oscilloscope shows an alternating p.d. with 4 complete cycles across 10 divisions, and the time base is 5.0 ms per division. Find the frequency. Is it the UK mains?

Show solution
  1. Time for 4 cycles: 10×5.0=5010 \times 5.0 = 50 ms, so one cycle takes 504=12.5\frac{50}{4} = 12.5 ms = 0.0125 s.
  2. Frequency =1period=10.0125=80= \frac{1}{\text{period}} = \frac{1}{0.0125} = 80 Hz.
  3. UK mains is 50 Hz, so this is not the mains supply.

The three mains wires

Most appliances are connected with a cable containing three copper wires, each covered in coloured plastic insulation, inside an outer plastic sheath. Inside a UK plug, they are arranged as below.

fuseneutral(blue)earth (green/yellow)live(brown)cable grip
  • Live wire (brown): carries the alternating potential from the supply. Its potential alternates, and the p.d. between live and earth is about 230 V.
  • Neutral wire (blue): completes the circuit back to the supply. It is at, or very close to, 0 V (earth potential).
  • Earth wire (green and yellow stripes): a safety wire at 0 V, connected to the ground. It carries a current only if there is a fault.

In normal use, current flows to the appliance in the live wire and returns in the neutral wire. The p.d. between live and neutral is about 230 V; between live and earth also about 230 V; between neutral and earth about 0 V.

Why the live wire is dangerous

Your body is at about the same potential as the Earth, 0 V. If you touch the live wire, there is a p.d. of about 230 V across your body, so a current passes through you to earth. A current of only a few tens of milliamps through the chest can stop the heart.

earth (0 V)live wire, about 230 Vcurrent throughbody to earthp.d. across body≈ 230 V

The live wire can be dangerous even when the appliance is switched off. An open switch only stops the current in the appliance; the cable between the socket and the switch is still connected to the supply and still at a high potential. If anything provides a connection between the live wire and earth (a person touching a damaged cable, a wet floor, a metal tool or a water pipe), a large current can flow through it.

Switches and fuses go in the live wire

Switches and fuses must be connected in the live wire.

switch in live ✓LNapplianceoff: applianceat 0 V, safeswitch in neutral ✗LNapplianceoff: appliancestill at 230 V
  • With the switch (or fuse) in the live wire: opening it disconnects the appliance from the high potential, so every part of the appliance is at 0 V and safe to touch.
  • With the switch in the neutral wire: the appliance stops working when switched off, but it is still connected to the live wire, so its wires and any faulty metal parts remain at 230 V. Touching them could cause a shock.

Practise this topic

Both are part of Premium.