Electrical power

Electrical power

Power is the rate of transferring energy. Combine the two definitions: in time tt a current II carries charge Q=ItQ = It, and each coulomb transfers energy VV, so the energy transferred is

W=VItW = VIt

and dividing by time,

P=VIP = VI

with PP in watts. Using V=IRV = IR (the definition of resistance, from topic 3B), you can derive two more forms:

  • substitute V=IRV = IR: P=(IR)I=I2RP = (IR)I = I^2R;
  • substitute I=VRI = \dfrac{V}{R}: P=V×VR=V2RP = V \times \dfrac{V}{R} = \dfrac{V^2}{R}.

Choose the form that uses what you know. P=I2RP = I^2R is the natural one for current through a fixed resistance (such as a cable); P=V2RP = \dfrac{V^2}{R} suits a component with a fixed p.d. across it (such as an appliance on the mains).

Worked example

A kettle

A 2.8 kW kettle runs on the 230 V mains for 3.0 minutes. Find the current and the energy transferred.

Show solution
  1. I=PV=2800230=12.2I = \dfrac{P}{V} = \dfrac{2800}{230} = 12.2 A.
  2. Energy: W=Pt=2800×180=5.0×105W = Pt = 2800 \times 180 = 5.0 \times 10^5 J. (Convert minutes to seconds.)
  3. Resistance of the element, if needed: R=V2P=23022800=18.9R = \dfrac{V^2}{P} = \dfrac{230^2}{2800} = 18.9 Ω.

Worked example

Why power is transmitted at high voltagetop grade

A village needs 50 kW. It is supplied through cables with a total resistance of 0.40 Ω. Compare the power wasted in the cables if the power is sent at 230 V and at 11 kV.

Show solution
  1. At 230 V the current needed is I=PV=50 000230=217I = \dfrac{P}{V} = \dfrac{50\,000}{230} = 217 A. Power wasted heating the cables: P=I2R=2172×0.40=1.9×104P = I^2R = 217^2 \times 0.40 = 1.9 \times 10^4 W, about 19 kW, which is 38% of what is delivered.
  2. At 11 kV: I=50 00011 000=4.55I = \dfrac{50\,000}{11\,000} = 4.55 A, so P=4.552×0.40=8.3P = 4.55^2 \times 0.40 = 8.3 W.
  3. Because cable loss depends on I2I^2, raising the voltage by a factor of 48 reduces the current by 48 and the losses by 482≈230048^2 \approx 2300.
  4. Trap: you cannot use P=V2/RP = V^2/R with V=230V = 230 V here, because 230 V is not the p.d. across the cables; it is the p.d. at the supply.
supplyvillage50 kWcables: 0.40 Ω in totalsent atcurrent I = P/Vlost in cables, I²R230 V217 Aabout 19 kW (38%)11 kV4.55 A8.3 W